Correction Factor for indirect cove light.

Hello!

In the old dialux, we used to have a correction factor for luminaires. In my previous office we used to consider a correction factor of 0.7 for indrect cove lighting. how do you take this factor into consideration in Dialux Evo? can seem to find a corrrection factot option.

Best reply by Daniel

Hello Elie,

such a correction factor has not been used for a long time. If you want, you can of course adjust the luminous flux of the luminaires (that's what a correction factor does), but I would advise you not to do that, because DIALux takes the room geometry and the reflectance of the room into account correctly anyway.

View original
5 replies